patricio_lintz

Jan 9, 2006, 4:25 PM
Post #2 of 2
(1756 views)
Shortcut
|
Ground & neutral have the same termination on the load center. They are both wired to the ground buss. The safety ground just provides an alternate safer path back to the ground buss in case of a hot wire to device body or elsewhere short. The question you ask depends on the configuration of the GFCI used. If it detects current flow in the safety ground, then no is the answer. If it is a type that sensenses an imbalance in current from the hot line to the neutral, then, it would work. However, it would be worth investing in installing safety grounds in all of your outlets to bring things up to latest US and international codes. The three wire sockets with the ground jack can be fooled so that the three prong LED circuit tester (available at Home Depot) passes it. Just wire the neutral to the ground jack. However, this is not recommended since it defeats the idea of an extra safety ground.
|